Dell PowerEdge T610 User Manual
Page 32
32
About Your System
E1717
CPU
#
internal
error. Review
& clear SEL.
The system BIOS has
determined that the
specified processor has
had an internal error.
Check the SEL for more
information and then
clear the SEL. Remove
AC power to the system
for 10 seconds and restart
the system.
If the problem persists,
see "Getting Help."
E171F
PCIe fatal
error on Bus
##
Device
##
Function
##
The system BIOS has
reported a PCIe fatal error
on a component that
resides in PCI
configuration space at bus
##, device ##, function
##.
Remove and reseat the
PCIe expansion cards. If
the problem persists, see
"Troubleshooting
Expansion Cards."
E1810
Hard drive
##
fault. Review
& clear SEL.
The specified hard drive
has experienced a fault.
See "Troubleshooting a
Hard Drive."
E1812
Hard drive
##
removed. Check
drive.
The specified hard drive
has been removed from
the system.
Information only.
E1A14
SAS cable A
failure. Check
connection.
SAS cable A is missing or
bad.
Reseat the cable. If the
problem persists, replace
cable.
If the problem persists,
see "Getting Help."
E1A15
SAS cable B
failure. Check
connection.
SAS cable B is missing or
bad.
Reseat the cable. If the
problem persists, replace
cable.
If the problem persists,
see "Getting Help."
Table 1-1.
LCD Status Messages (continued)
Code
Text
Causes
Corrective Actions